scp Posted February 21, 2023 Report Posted February 21, 2023 Hi. Do you need to link an existing alarm system from a ground floor commercial premises to a first floor flat above. Quote
AnthonyB Posted February 22, 2023 Report Posted February 22, 2023 Only if the structural fire compartmentation between the two is inadequate and it's not viable to upgrade it. Usually the requirement is 60 minutes fire resistance. (This assumes the flat has separate access not via the shop) Quote
Recommended Posts
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.