Jump to content

Flats over empty commercial units


Recommended Posts

Guest Clare Smart
Posted

Can anyone help me.  I've been asked by a client if they could avoid the expense of providing 60 minute fire rated boarding between their commercial units and the flats above, if the commercial units became empty?  I can't find any particular guidance around this and wonder if it just comes down to a risk assessment?

Any help would be appreciated.  Many thanks.

Posted

It would be down to risk assessment - empty does not mean risk free (which is why vacant premises are not exempt from the Fire Safety Order).

I'd be looking at things including:

 

  • Removal of all combustible materials and waste
  • Isolation of gas & electricity
  • security against arson & unlawful occupancy

as part of determining if it was tolerable or not

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...