Hi

I was asked to wire a magnetic door lock into a fire alarm system, I know that it has to be wired to the fire alarm panel but the company who installed the magnet door lock has mentioned that it can be wire to the nearest call point via an electric interface devise or I/O, is that true? if yes can anyone give me some more info please?  

Posted

If the fire alarm is addressable then it may be possible to add an I/O interface. But it would be a job for the fire alarm company to do. It also depends on the make of fire alarm as to if it will accept an I/O device.

Posted
On 08/08/2022 at 18:20, Guest Med said:

Hi

I was asked to wire a magnetic door lock into a fire alarm system, I know that it has to be wired to the fire alarm panel but the company who installed the magnet door lock has mentioned that it can be wire to the nearest call point via an electric interface devise or I/O, is that true? if yes can anyone give me some more info please?  

The interfacing needs to meet BS7273-4 which most lock/security companies seem to be oblivious of. If you aren't qualified to work on fire alarms you shouldn't really do it.

I can't attach the standard for copyright reasons, but this extract from building regulations summarises requirements:


Electrically powered locks should return to the unlocked position in all of the following situations.
a. If the fire detection and alarm system operates.
b. If there is loss of power or system error.
c. If the security mechanism override is activated.


Security mechanism overrides for electrically powered locks should be a [Green] Type A call point as described in BS 7273-4. The call point should be positioned on the side approached by people escaping. If the door provides escape in either direction, a call point should be installed on both sides of the door.

image.jpeg.0c8d9b709579dfb5ea698d1e35483ffd.jpeg

Fire Alarm connections

1 - Conventional system using control panel's relay
image.png.7d346434c7230ae76ac572eb4381ca3c.png

2 - Addressable system using i/o unit on the loop (also requires programming on the panel, not just a physical job)

image.png.f23d6973eb78fd9226d295bbf951220c.png

Posted
On 22/08/2022 at 01:05, AnthonyB said:

but this extract from building regulations summarises requirements:


Electrically powered locks should return to the unlocked position in all of the following situations.
a. If the fire detection and alarm system operates.

 

Of course I understand the rational for this clause, but where green boxes are used to secure a final exit, surely having the external door unlock when the fire alarm operates is a security risk
 

If intruders create smoke and introduce it into the building at 2am or on a Sunday,, all final exits open and they are in

Posted
18 hours ago, Hayfever said:

Of course I understand the rational for this clause, but where green boxes are used to secure a final exit, surely having the external door unlock when the fire alarm operates is a security risk
 

If intruders create smoke and introduce it into the building at 2am or on a Sunday,, all final exits open and they are in

There is scope not to have this link in places of detention, certain healthcare scenarios, etc but the default for normal premises is to interface as life is considered more important in the regulatory framework. It's up to the Responsible Person to ultimately decide as legally they carry the can. 

Posted
18 hours ago, AnthonyB said:

There is scope not to have this link in places of detention, certain healthcare scenarios, etc but the default for normal premises is to interface as life is considered more important in the regulatory framework. It's up to the Responsible Person to ultimately decide as legally they carry the can. 

This is exactly the set up I help establish for a range of secure buildings where is was untenable to allow such circumstances where people externally could nefariously open final exits and gain access, even with intruder alarm operation.

We added mitigation of monthly manual override tests (on a rota of a small number per week which meant all units were tested in a 4 week period) plus additional signage, plus 2 fire drills per annum 

 

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...