Guest Andy Posted May 4, 2012 Report Posted May 4, 2012 Hi In warehouses what distance should stock be stored from sprinkler head? Thanks Andy Quote
Tom Sutton Posted May 4, 2012 Report Posted May 4, 2012 I have never been involved closely with installation of sprinklers but the British Standard is BS EN 12845:2004+A2:2009 Fixed firefighting systems. Automatic sprinkler systems. Design, installation and maintenance. For Further information go to http://www.firesafe.org.uk/industrial-fire-sprinklers/ Quote
Tom Sutton Posted May 5, 2012 Report Posted May 5, 2012 Andy check out http://fire.org.uk/forum/index.php?topic=5779.new#new and you will see it becomes quite complicated. Quote
Guest Pierre Paul Posted June 14, 2012 Report Posted June 14, 2012 According to NFPA 13, the sprinkler distance from top of storage to the sprinkler heads for traditional heads is 405 mm. For ESFR heads, it is 0.9m Regards Pierre Quote
Tom Sutton Posted June 16, 2012 Report Posted June 16, 2012 Be careful NFPA 13 is an American Code and there can be a variance between there codes and European standards. Quote