Hi, just trying to establish testing requirements in sheltered housing. I know part 1 system Grade A requires testing weekly and 6 monthly service. Grade D again weekly service annually.
But when it comes to the Part 6 Grade D system within the flats. I am not sure of what the testing frequency is.
specialised housing says monthly and so does BS5839-6.
But if ARC is installed in the flats then how often should these be tested??
94.16 Where the fire strategy for the building relies on remote transmission of signals from detection within residents' accommodation to an alarm receiving centre (ARC), at the time of the weekly fire alarm test, transmission from the accommodation of at least one resident should be tested to ensure that the signal is received correctly at the ARC. This test should be carried out from the accommodation of a different resident in each successive week, so that, over a period of time, transmission from all residents' accommodation is tested. There is no maximum time over which this should be carried out (i.e. if there are 30 flats in a sheltered housing scheme, it will take 30 weeks for transmission from all flats to be tested).
Does this mean on the weekly communal test that weekly tests on flats with telecare should also be carried out on one of the flats and test a different flat each week until done.
The flats we have are independent flats grade D no telecare then we have flats that part of the main building and have telecare installed. These activate at the ARC centre and notify the manager but not linked to the part 1 communal system.
The way I interpreted this is monthly for the independent flats, then the scheme flats tested with the main alarm system. So if we had 52 flats a different one would be tested each week so over the 52 weeks they all would have been tested over the year.
I don’t know if I have interpreted this incorrectly, but if not seems strange the independent flats are monthly and potentially the other flats yearly or possibly twice a year if less flats.