Assisted Living Fire Safety - Door Spec Recommendations
Have you thought of a free swing door closer TS 5000 RFS 3-6 | GEZE
-
Does it need to be a Fire Door?
A storeroom does not necessarily need a fire door, it all depends on the flammability of what is so be stored in the room, cardboard and spare furniture I would not regard as a major risk as long as it is controlled and does not become a dumping ground. If the distribution board is in a fire rated enclosure, then there is no need to put it behind a further fire door. Use a camera to take a picture of the top of the door, it may be a fire door, just not set up as one as the cost of the doors are not that different. The major difference is the sealing and inspection.
-
MEK storage/usage
The door could be an older type that does not require intumescent strips. it will have 1” door stops instead. But is sounds like it wants replacing The vent through the door is acceptable with an intumescent grille as long as the door is not a smoke door, if it is then you need a damper in the door connected to the fire alarm. What is more concerning is the cleanliness of the area, it sounds like there is a risk of spontaneous combustion of the discarded rags. Flammable liquids should be kept to a minimum in the work area, no more than that required for the current shift. See the attached Storage of flammable liquids in process areas, workrooms, laboratories and similar working areas - HSE
-
Fire stopping penetrations with fire rated plasterboard
If it has been installed correctly, there is nothing wrong with using fire rated plasterboard to repair (any plasterboard patch repair in a fire-rated wall or ceiling must fully restore the original level of fire resistance). It would make sense however to use something like Intumescent Pillows - FireSealsDirect on cable trays as it will make maintenance easier should they need more cables run.
-
Window in protected stairwell.
If the window is located in a protected stairwell, it should be fixed shut and achieve a fire resistance rating at least equal to that of the wall in which it is installed.
-
Fire exit signage
The importance of wayfinding signage is not for the occupants but the fire brigade who will be entering a smoke-filled building possibly in the dark. They cost pennies
-
Additional measures for EV charging in car parks
The current thoughts are that the probability of an ICE fire is 1,500 fires per 100,000 vehicles, for EV’s 25 fires per 100,000 vehicles. The issue is that when an ICE car is involved in a fire there is limited fuel and a lower temperature 800 to 1000 C for an EV up to 1200 C. 02.3 Key findings | EV Fire Safe
-
Fire door assessment prior to maintenance
Yes and no. If its running maintenance such as replacement seals, minor gap adjustments, like for like replacement of door furniture etc then yes. Anything else should be assessed, don’t forget that a temporary repair is better than leaving a defective door whilst waiting for a replacement.
-
Timber Doors in Aluminum Frames
This looks like an office door and has no fire door signage. Have you looked at the strategy for the building as sometimes the builder will install fire doors where they are not required so they all look the same. See ADB para 2.24, 2.25, 2.27 to see if it needs to be a protected corridor. If they are fire doors then they need 3 hingers
-
Is FRA Required
For a single dwelling Private renting: Your landlord's safety responsibilities - GOV.UK however since you have stated that their is also a basement flat then yes you need a FRA. the front doors would be assessed as part of the FRA
-
Office building with living accommodation above - who is responsible for the interlinked system
Who is responsible for the installation is a legal question.
-
Correct use of fire foam
Personally I hate this stuff, it is very rarely used correctly. The rule of thumb is that when installed the depth should be at least 10 times the width, basically narrow linear gaps. If you do use it then you must get the certfire certificate for the product to see how it should be installed and the gaps that it can seal.
-
Fire door regs for 3-storey flat blocks under 11 metres
1. The sealing of electrical cables, where the cable enters or exits the riser should be stopped. 2. If they are serviceable and are manufactured from solid metal with a melting point of at least 900C, then no 3. I agree with the inspector, you should put in program to bring the doors up to nominal standard, prioritising smoke (look at batwing or combined seals) and gaps. Fire doors should have 3 hinges, however if the door is small an exception can be made. Can you ignore it, yes, however, you should come up with a written answer to all the defects and how you propose to rectify or compensate for each. Should anything happen, the first port of call will be the FRA, the next will be a man with a curly wig asking you why you ignored the FRA. For fire door inspections If a flat owner or resident refuses to allow a fire door inspection, they are potentially hindering a legal safety requirement under the Regulatory Reform (Fire Safety) Order 2005. Fact sheet: Fire doors (regulation 10) - GOV.UK
-
Fire doors in a domestic 3 storey house
A self-closer is no longer required, however care should be taken when filling the holes as the door should be still a FD20 if it is on a protected route
-
Riser cupboards and communal doors in a 2 storey residential block built in 2005
Yes ADB only applies to new builds and material alterations, however the RRO and following a small fire in London, the Fire Safety Act 2021 enforce general fire safety of existing buildings. The regulations have not distally changed with respect to smoke control for communal doors or riser doors, in the past 25 years. Given the age of the building, I would have thought that a gap of 6-8mm the doors were never to standard.
-
Air Pressure issues and Fin strips as a solution
have you tried removing the smoke and instilling batwing seals
-
Fire door sign on door leading edge
ADB C12 The following fire doorsets are not required to comply with paragraph C11. a. Doors to and within flats and dwellinghouses. b. Bedroom doors in ‘residential (other)’ (purpose group 2(b)) premises. c. Lift entrance/landing doors.
-
School kitchen hatch fire shutter
What exactly does the FRA say? Is it about the panel or the rating of the shutter
-
NFR Rated Door - Remedial Works
Check the original as built fire strategy as office doors do not usually need to be fire rated (except dead ends, high risk areas etc). It may be that at some point in time someone has put fire signage on the doors Protected corridors 2.24 A corridor serving as part of the means of escape in any of the following circumstances should be a protected corridor. a. Every corridor that serves bedrooms b. Every dead-end corridor (excluding recesses and extensions a maximum of 2m deep, as shown in Diagrams 2.7 and 2.8). c. Any corridor shared by two or more occupancies (paragraph 2.17). Enclosure of corridors that are not protected corridors 2.25 If a corridor is used for a means of escape but is not a protected corridor, even though the enclosing partitions may have no fire resistance, both of the following should be met to inhibit the spread of smoke. a. Partitions should continue to the soffit of the structural floor above, or to a suspended ceiling. b. Openings into rooms from the corridor should be fitted with doors, which do not need to be fire doorsets. Open planning will not inhibit the spread of smoke, but occupants can become aware of a fire quickly.
-
PAUL ROGERS
Without knowing the building it’s impossible to answer, but as a rule of thumb, if it is possible for smoke to affect the escape route then there should be smoke seals. The cost difference between smoke and not smoke is negligible. The who is responsible for the cost is a matter for the tenancy agreement and is not a fire safety issue, but ultimately, I suspect that it will fall on the leaseholder
-
What gap under fire door
The maximum gap for a smoke door is 3mm. It may be possible to fit a threshold seal, but I have never come across one that would bridge that gap It may also be possible to lip the door, but again I have never come across one that would bridge that gap You could put a 17mm hardwood threshold detail under the door fixed to the floor, but that may cause a trip hazard
-
Management co demanding new flat doors
A 15-year-old door would be as compliant with the latest regulations as when it was installed, the regulations for fire doors have not changed, however, there is no guarantee that the doors were compliant then installed or that the doors have not been altered that would make them uncompliant. You should ask the agent why they are not compliant, it may be a latent defect which may be there responsibility
-
Childrens Home Fire safety Guidance
All DCLG guides can be found here Fire safety in the workplace: Fire risk assessments - GOV.UK
-
Fire doors/Storage on protected stairway
Read and inwardly digest for the risks involved leaving fire doors open Rosepark care home deaths 'preventable' inquiry finds - BBC News
-
FD30 vs FD30S for Block of Residential Flat built in 2017-2020
Correct, flat doors should be FD30S, this has been the case since at least December 2018. To comply, the head and side gaps should be 3mm ±1mm (irrespective of smoke). The threshold on a smoke door should be a maximum of 3mm. I suspect that the door was never compliant in the first place.