  1. Correct, flat doors should be FD30S, this has been the case since at least December 2018. To comply, the head and side gaps should be 3mm ±1mm (irrespective of smoke). The threshold on a smoke door should be a maximum of 3mm. I suspect that the door was never compliant in the first place.
  2. Legally, as long as they are competent, anyone can do it, but it must be correctly installed (the inspector will fail it again if not)
  3. The door should be routered to accept the intumescent strips, they should not alter the door gap. The smoke fins can sometimes bind, some Vaseline can be applied to soften the blade
  4. It all depends on the size of the enclosed area and the risk. If the area is big enough you can call it a place of ultimate safety, but technically it should allow for the restricted dispersal of people
  5. For anything above the second floor, you are more at risk of serious injury or death from jumping out of the window than the fire itself. A decent alarm system should notify you long before the escape route becomes untenable, if the fire is on the other side if the door, you will have a minimum of 30 minutes for the fire brigade to rescue you
  6. A guide to making your small block of flats safe from fire (accessible) - GOV.UK
  7. The use of magnetic hold open devices kind of defeats what the regulations are trying to do here. Without seeing the doors, I suspect you have 2 options; 1. Change the swing of the doors 2. Limit the occupancy of the room
  8. For multiple doors try Our Services - Fire Doors - IMS Group - A Specialist Passive Fire Protection Company
  9. You could take a general image of the area to show the general location, then a close image of the label details before you remove the labels
  10. You may get certification to say that the building was built to building regulations, however a building that was built in the 1980s it does not mean it comply with the current building regulations. Any alterations or maintenance to building would make the original certification null and void as what was signed off is not what was is there now. You need to look at the regulation 38 information, which should be an up-to-date record of all the fire safety information for the building Including fire doors along with the latest FRA and any recent fire surveys to get an holistic view.
  11. look at the installation instructions for the door, some can some can't
  12. Building regulations can only be applied to new buildings or material alterations whilst they are being built, can you imagine the cost of bringing Windsor castle up to date? You won’t get certification to say it meets the regulations. Once a building is built and handed over, building regulations are out of the window except for material alterations. The fire safety order then comes onto force which (amongst other things) requires the responsible person (or their agent) to conduct a fire risk assessment on the building and address the findings. It is not a money-making scheme, If the glazing says it is fire rated, then unless the assessor can prove it isn’t then it’s acceptable
  13. To certify a repair to a fire door you must know what the original certification was and what is allowed to be done to the door under the certificate if approval. I also don’t think that this would be covered under an Approved Repair Technique
  14. Possible solution is a free swing closure such as Briton 996 Hold Open Free-Swing Door Closer
  15. I assume that the removed closers where Percos? Why did you not just cut the chains, problem solved. I don’t think you could certify a repair
×
×