  1. Magnetic locks fitted to timber-based fire doors should be suitable for and compatible with the fire door. Consult the product certification data sheets for the maglock and for the fire door, for suitability and compatibility with eachother.
  2. The lock appears to be located at the top of the closing edge of the fire door and bears no marks indicating its suitable for a fire door? Usually the evidence of fire resistance performance for a timber fire would state that the lock position should be between 800mm and 1200mm from the door bottom edge. The lock forend dimensions seem quite large too. There also appears to be a magnetic lock fitted? If that's so, is it suitable for and compatible with the fire door?
  3. This is a question for an architectural ironmonger. Try a GAI member. Is the door really a fire door?
  4. Where has the 'instruction to replace them' come from? What authority does the instruction carry? Has a suitable and sufficient Fire Risk Assessment been carried out and if so what was concluded with respect to the four cupboard doors? The answers to these questions will help the freeholders make the decisions.
  5. Looks like a timber-panel door and therefore most likely not traceable to evidence of fire resistance performance. Your next 'go to' would be technical fire resistance performance data for the glass itself and most GWPP would most likely have been manufactured by Pilkington as the product 'Pyroshield' or its forerunner. Many would accept this type of fire door as 'Nominal or Notional'. Where you cannot satisfy yourself of suitable product performance, a Fire Risk Assessor should be able to advise in terms of the suitability of a fire door with unknown ultimate fire performance given the location of the door and the fire strategy at the building.
  6. The gaps of 4mm to 6mm would most likely never have been compliant. The current hinges may be compliant (with building regulations Approved Document B) where the melting point of the materials they are made from exceeds 800 deg C. Each flat entrance door should be fitted with suitable smoke seals and intumescent edge seals. So there are clearly some defects with the fire doors that may allow fire and smoke to spread from the flats and into the escape routes in a fire situation, before the minimum thirty minutes required by building regulations (ADB). The Fire Risk Assessor at the building should decide what remedial works should be undertaken and at what priority in terms of the fire strategy at the building.
  7. Not allowed because it fails to automatically release when the fire/smoke alarm is activated.
  8. The issue with plastic signs stuck to the non-fire side of a non-insulating door (eg metal or glass) is that heat transfer could cause the sticker to ignite.
  9. It would be a specialist product https://www.thepocketdoorcompany.co.uk/product/classic-single-fire-rated-pocket-door-system-copy-2/ rather than something you would assemble using various component parts.
  10. If the defect is that the closing edge gap is 8mm, then the correct way to rectify the defect is to remove the door assembly or at the very least loosen the door frame closing jamb and reinstall the assembly or pack the closing jamb as necessary to reduce the gap to between 2mm and 4mm. Then it will be necessary to tighten all fixings maintaining correct gaps and alignment before correctly fire-stopping the gap between the door frame and the supporting wall. Refer to 'BS 8214: 2016 Timber-based Fire Door Assemblies - Code of practice' for support.
  11. Based on the use of the self-closer above and assuming that the fire door leaf has evidence of fire performance in an unlatched configuration, the door could be unlatched. Correct installation of the self-closing device is key to performance for 'hold-shut' as well as self-closing performance.
  12. Whilst there is no mandatory requirement for certification, fire door installers should be competent persons. https://www.legislation.gov.uk/uksi/2005/1541/article/18/made If you are interested in fire door installation training https://www.firedoorscomplete.com/training-qualification
  13. Flat entrance doors opening onto communal areas inside the block would be FD30(s) and self-closing as a minimum. Refer to BS 8214: 2016 Timber-based Fire Door Assemblies - Code of practice for guidance on smoke seals and threshold gaps and seals. https://bookshop.bmtrada.com/bookshop/view/1f43261a-1100-489d-8c5e-f4673ff17739
  14. The door leaf manufacturer will advise whether such a device is permitted as well as the position for the middle hinge. The self-closer manufacturer's installation instructions will provide the details about the position of the self-closer in connection with the middle hinge.
  15. https://www.firedoorscomplete.com/training-qualification
  16. Its a question for the 'inspector' but if you can demonstrate that you have carried out the works in accordance with the wired glass manufacturer's requirements, that should be acceptable. https://mbp.co.uk/wp-content/uploads/2021/05/PYROGUARD-CF5954-Pyrostem-exp.20260524-rev.20210525.pdf https://www.pilkington.com/en-gb/uk/products/product-categories/fire-protection/pilkington-pyroshield-2 Above are only suggestions as we don't know which product the wired glass is and when it was made. Where you are unable to identify the glass, you should use best practice methods https://shop.ggfmembers.com/a-guide-to-best-practice-in-the-specification-and-use-of-fire-resistant-glazed-systems-ref-20-1/ and https://www.ggf.org.uk/about-the-ggf/contact/
  17. Yep. In this context, better to lip the bottom rather than the top.
  18. Always difficult with non-intrusive inspection and when there's no evidence. In terms of guidance https://www.local.gov.uk/sites/default/files/documents/Fire Door FAQs.pdf
  19. For certainty on this matter, always contact the door leaf / door blank manufacturer for advice. There isn't much in the way of information on-line on this particular subject but this is quite helpful: https://www.falcon-timber.com/downloads/ Typically guidance on applying facings might look something like this:
  20. Q2). A couple of doors have maglocks that have been bolted through the door. There is no information on the door. The inspector recommends new doors as there is an integrity breach. Can maglocks be removed & door repaired? ( 2- I'll let the forum's fire door specialist address this next time he logs on ) : A) There are some timber-based fire door / magnetic lock combinations that do have evidence of fire resistance performance. So, it may not be appropriate for the mag-locks to be removed / fire doors replaced - it would depend on the type of door leaf construction and the type of mag-lock. I would advise that first a risk assessment should be carried out to evaluate the risk to life safety and building safety were the fire doors to fail to provide their ultimate fire resistance performance as designed. Where the risk is untenable and a certificated solution is required then the fire doors should be replaced with a set that are suitable for mag-locks. If the mag-locks are no longer required and it is felt that the doors do not require certification and can be repaired - then the repairs to the door leaves and frame should be made to a joinery standard using suitable hardwood tightly fitted with no holes, gaps or voids.
  21. Begin with the self-closer manufacturer, the may be able to put you in contact with a door manufacturer that has dual certification using their self-closer.
  22. Yes, as you have picked up - the lipping must be flush with the face of the door. So lipping may be replaced or added to the edges of the door but the hardwood must be of the correct dimensions, species, density and fitted with the correct adhesive. This type of 'repair' is very likely to fall outside the scope of the fire resistance performance certification for the door and therefore the certification would become invalid.
  23. Before you fill that gap with intumescent or non-combustible material check that: The fire door leaf does not sit proud of the door frame at any point. Have the hinges been checked for compatibility with the fire door leaf, in terms of fire rating and dimensions? Are these 'extended butts', are the fire doors intended to open to 180 deg?
  24. https://www.safelincs.co.uk/fire-door-installation/
  25. The product data sheet or installation instructions for the door leaf will advise what materials are permitted for the door frame.
×
×