  1. If you are purely a damp proofing firm then you shouldn't be messing with fire doors as the trades are not related. If you don't have competent trained staff with the correct tools and consumables then there is a big chance that you will not do it correctly and everyone looses in the long run. I've seen work by joiners that is abysmal and non compliant or using completely outdated techniques that go back to the 60's & 70's door standards and would want work to be done by an accredited specialist. Stick to what you are good at.
  2. These are all ABC Powder!
  3. Extinguishers are not provided for means of escape, that's an old myth, but to mitigate the effects of fire and if one fails you get out. The risk of failure is minimal if you have a suitable system of maintenance and buy decent quality kit.
  4. Because some people follow common sense (& risk assessment) and do not rigidly follow the recommendations of BS5306-8 which has been ruined by the trade representatives on the Committee to sell extinguishers. If it's a floor area under 400 sq.m. then in some circumstances the potential 4 extinguishers per floor (if you use separate CO2 for electrical risks) is just plain overkill, especially in premises small enough for a single exit.
  5. Which would potentially still be wrong, just not under fire legislation!
  6. Most UK extinguishers contain ABC (General or All Purpose) Powder based on mono-ammonium phosphate & sulphate - usually yellow (but with far east imports you can get blue, green, orange/pink). It is slightly acidic and fuses into a sticky flux when hot (which is how it is effective on Class A solid fires by coating embers) This powder as a result has a high secondary damage potential to delicate items, electronics & machinery. It is non toxic, but mildly irritant. A small number of aerosol and small automotive extinguishers contain BC (Standard Powder) which is Sodium Hydrogen Carbonate and usually white. It is slightly alkaline (hence it's use in kitchens before the development of wet chemical as it had a slight saponific effect on cooking oils). It does not flux and has less damage potential, is easier to clean and less irritant. It is not effective on deep seated Class A fires as it does not flux around embers. Specialist BC powders exist for high risk environments (Potassium Bicarbonate "Purple K" and Potassium Allophonate/Potassium Bircarbonate/Urea Complex "Monnex") but these are not found in general use due to cost. BC & ABC Powders main extinguishing effect is by chemically interrupting the chain of combustion with little appreciable cooling or smothering effect so there is a risk of re-ignition after use and with a Class B fire if you don't extinguish it all in one go the fire can instantly re-flash to it's original size. Class D fires (flammable metals) have specialist powders, choice dependant on the metal involved - these use Sodium Chloride, Graphite or Copper to absorb heat and flux over the metal allowing it too cool. Where US terminology is used instead of UK then ABC & BC extinguishers are called Dry Chemical with the term Dry Powder being used only for Class D agents.
  7. If it's a means of escape Building Regulations doesn't usually allow electro-mechanical locks such as electronic keeps, but prefers electromagnetic locks. If however there is an internal means of unlatching the door without operating the keep/strike (tumbturn operated deadlock latch or a night latch [Yale lock]) then it's OK as releasing the door does not rely on the electromechanical part of the access system.
  8. Your fire risk assessment would have to justify why deviating from the benchmark of weekly testing would not lower the standard of life safety of the relevant persons. It's possible, that's the point of risk assessment, but you need to back it up as enforcers will initially look for weekly tests unless you convince them why monthly is OK
  9. Traditionally the maintenance standards required you to leave the relevant service history of the extinguisher from a previous provider visible, but currently you have the option of covering it if you transfer ALL relevant service history over (commissioning, weight, date for OH/ES etc)
  10. Some care homes (particularly those where dementia & other mental disorder service users reside) have the local overrides and no fire alarm interface to facilitate controlled evacuation as if all the doors (including final exits) fail open at the same time there is a real risk of service users wandering off out and coming to harm. Building Regulations requires the trinity of failsafes on mag locks - power failure, fire alarm interface, local double pole break glass override & the DCLG risk assessment guides list them also. Risk assessment can potentially dispense with some of these, but must justify why this is acceptable and not an increased risk.
  11. The age of the property (and the age of construction of the garage if not an original feature) will determine whether there is no fire door, a notional fire door (rebated no strips) or a current FD30S door. Most minor domestic building work won't go through Building Control even though it should, so it sounds like your extract was put in under the radar using random components
  12. By residential do you mean care home or a former private house used akin to a HMO? More opinions would be gained from asking this on Firenet: https://www.crisis-response.com/forum/
  13. It's not just the door that needs to be a fire door - if the stair is wooden it needs underdrawing with a suitable layer of fire boarding (usually plasterboard of at least 12.5mm or glass reinforced gyspum sheeting of at least 10mm) suitably secured to a metal or wooden stud with edges sealed with fire mastic
  14. AnthonyB

    Exit Break Glass

    "Doesn't look nice" isn't enough justification. The other location would allow escape without passing a call point and so the system could not be certified as compliant with BS5839-1:2013 unless the location was agreed and recorded as a variation, but it would need to be agreed with all relevant parties - fire alarm engineer, risk assessor, client and Building Control (as it sounds like 'building work' under the Building Regulations has been carried out)
  15. Grade 4? No such thing unless you mean L4 3 wire with call points sounds like an old system in a commercial building, either 240 v or 24v off a separate charger and battery box, either with a separate indicator panel, just a diversion relay, or nothing other than the mains switch. It could have been partly updated by adding a 'modern' style control panel which may by itself now be getting in age. You can still get 3 wire compatible replacement panels and if you need detection you can run a new two wire zone for the detector heads. All new cabling will need to be fire resistant. You can't remove call points, the base system required for premises is a manual system of call points, detection is an extra where required by the premises layout, risk and usage (e.g. sleeping risk) You can add pictures on this forum so images of what you have (cable, call points, panel, etc) that would help.
  16. Fire drills are not normally considered appropriate in residential sleeping risk such as HMO's and flats, even when a fire alarm system is fitted. The main requirement is that the evacuation strategy (evacuate or stay put) is clearly communicated to and understood by all residents.
  17. This is the benchmark guidance for flats - as you will see there is some leeway for smaller older blocks: http://www.local.gov.uk/c/document_library/get_file?uuid=1138bf70-2e50-400c-bf81-9a3c4dbd6575
  18. 1l Water mist or a 2l P50 foam or a 3l ABF rated wet chem all sound better alternatives to powder. An obsolete 9 litre water jet and a CO2 would be not advisable either
  19. Smoke detectors on a commercial intruder alarm are not for life safety and are for property protection out of hours via the intruder systems dialler or Redcare link. If your premises are so large a shout of fire, hand operated gong, whistle or similar cannot be heard throughout the premises without putting persons are risk then an electrical manual fire alarm system using call points and sounders to Category M of BS5893-1 is required. This is the legal benchmark and in simple non sleeping risk premises you do not require any detection unless there is a risk of a fire going undiscovered for long enough to prejudice escape - most single occupancy premises don't need this as they are usually occupied such that the staff would readily discover a fire early on and activate a call point (human senses are better detectors than you might have thought) Smoke alarms are for residential use, not commercial, although there are a few applications where they may be used, such as for inner room situations where only a local alarm is needed of a fire in an access room.
  20. Sounds like you don't have the proper Theatre exit signs that are designed to have low ambient light levels and limited light spill during normal maintained mode and only full brightness in emergency mode. (e.g. http://www.escapezone.net/assets/pdf/Escapezone-st43m.pdf) You can't physically just turn maintained lights off, unless they have been set up as switchable maintained (not usual, but not unknown). Even if you can you shouldn't, but subject to suitable management backed up by a risk assessment it's not impossible for such a short time
  21. If this had been thought of in the design stage then either traditional central battery or addressable LED emergency lighting systems could have been specified - with these individual fittings are powered centrally so there would be no LED in the fitting to cause disruption. As you are stuck with self contained fittings you may need to consider replacement with different fittings where the LED is placed to be less intrusive - with some I see it's quite hard to see the LED
  22. I'd be surprised if it was as well. If your lease doesn't include an easement for this usage and there is no deed of variation for escape access you can keep it locked in the short term whilst you sort it out. If a recent build I'd ask to see the fire strategy that contains this route and the proof of Building Control approval. I'd also ask the fire service for advice - fire regulations require premises to have escape routes not requiring fire service assistance and a 4th floor dead end balcony requiring the fire service to come along with ladders or an aerial platform would not meet this criteria. I'd also ask for a copy of the fire risk assessment - it may not be suitable and sufficient - just because a panic bolt has been fitted doesn't make it a fire exit, I've seen doors that are definitely not part of an escape route with panic bolts on. Of course it could be as simple as the panic bolts having been fitted on the wrong side of the door and that they should be on your side giving you emergency access to the shared stair (possibly as you may have a flat internal layout requiring the second route)
  23. The issues are if the buggy would be an obstruction and whether it poses a fire risk in what should be a fire sterile area by way of it's fabric coverings. The default would be a no to storage, but depending on the answers to be above and the options for managed use of the communal areas some storage occurs in some premises
  24. Possible, but unlikely. Some traditional fire extinguisher companies do carry out Extended Services on liquid extinguishers, but most will replace new as the trade cost 'out of the box' is comparable with the cost of an Extended Service once you've thrown in labour time, environmental compliance, and the cost of having all the parts, chemicals and charging equipment on every van. Plus it's years and years and years since engineer's training courses included recharging so there is a large number of engineers that don't know how to fill an extinguisher. You are looking at time to take the extinguisher to the van finding a suitable foul drain for legal discharge if the van has no agent tank a minute to empty the extinguisher a minute or two to remove the valve a few more minutes to strip the valve & change the O-ring and to rinse out the body (and where do they get the water to do this if they are at the van?) Another few minutes to blow the hose and dip tube and change the O-ring A few more minutes to refill the body with water (from where?) add the wet chemical concentrate and refit the valve A minute or two to fit the charging adapter, connect the Nitrogen cylinder in the van and pressurise the extinguisher and reassemble the hose A minute or two to fit the pin, pull tag, test the pressure gauge and affix the dot and to fill in the service label Time to bring the extinguisher back into the premises I would suspect the extinguisher was taken to the van, labelled as Extended Serviced, and brought back........
  25. If you are genuine trade you should be able to go direct to manufacturers - Jewel Saffire, PJ Fire, Jactone, Britannia Fire, Express Fire, Check Fire, Moyne Roberts, TG Products. These can supply all the correct servicing spares and tools too. If you are a small quantity user then you may actually get a better deal via Safelincs as some manufacturers have different pricing structures based on turnover and Safelincs, who due to turnover will be on the best scales the manufacturers they use offer, may actually offer better rates than direct!
×
×