The 2005 Fire Safety Order explicitly excludes dwellings and only covers parts in common such as the external wall in your property. If they are an owner occupier fire safety is solely their problem. As long as your renovation complied with Building Regulations (or if outside the scope of where approval is needed didn't make the original provisions worse) you are fine.
-
Yes, especially as they don't from your description appear to be approved for fire doors. The integrity of the door could be affected, also depending on the situation the door might not meet exit fastening standards.
-
If it's small and only is likely to contain less than 60 persons then the normal entrance alone may suffice. Your Fire Risk Assessment (which you are legally obliged to complete) would determine this applying the benchmarks in this document: https://www.gov.uk/government/publications/fire-safety-risk-assessment-offices-and-shops
-
No, the "mains on" LED is an integral part of the fittings. I have heard anecdotally some of the downlighter versions can have it disabled but can't confirm this. It's up to the Responsible Person to decide if they want to obscure this as they are legally liable - it has been argued that as long as the required monthly and annual testing regime is in place this would suffice - some places have increased the function testing to weekly as mitigation. Any deviation would need to be justified in the premises Fire Risk Assessment as to why it doesn't prejudice the safety of relevant persons.
-
It would have been Approved Document B as it has been since 1991 - the 2000 edition would apply. Past editions are here https://www.planningportal.co.uk/applications/building-control-applications/building-control/approved-documents/part-b-fire-safety/previous-editions
-
Large fire in house and amount of extinguishers
AnthonyB replied to Ademco's topic in Fire Extinguishers
It was not unusual in the past for multiple extinguishers to be used on fires almost in a bucket chain of them - and one major manufacturer from the 20th Century advertised how a use could refill their extinguishers in 30 - 60 seconds max to allow a continued attack on the fire. Works brigades or works fire teams were not uncommon and many fires were extinguished or controlled this way with anything from one to a dozen extinguishers used. Society is far more risk averse these days hence the approach you are hearing. However that doesn't stop you deciding to do what you feel best and have the kit for a prolonged attack as long as you don't put yourself in danger by following basic fire fighting practice (e.g. stay low, keep a exit behind you, etc) -
By definition a Grade D alarm is powered by a 240V supply, the 1 or 2 defining if the back up supply also required to each alarm is a sealed tamperproof battery/cell or a user replaceable battery. If you only have the built in power supply and no mains then it is only a grade F alarm (which can only be used in a rapidly decreasing number of situations) being a F1 or F2 again depending if the (sole) power is from a sealed tamperproof battery/cell or a user replaceable battery.
-
Is this an external gate not in the actual building? Does sound rather OTT and not covered explicitly by an actual regulation.
-
That's really one for your fire risk assessment however from the guidance for Specialised Housing it says: The extent of automatic fire detection should comply with the recommendations of BS 5839-6 for a Category LD1 system (which is the highest category for protection of life in domestic premises). Smoke detectors should be provided in all circulation spaces, and in all rooms within the property, other than kitchens, toilets, shower rooms and bathrooms. In kitchens, heat detection should be provided. However, where a kitchen or dining room forms an inner room accessed only from the lounge, the detector in the inner room may be omitted (rendering the system Category as LD2). No fire detection need be provided in toilets, shower rooms and bathrooms or, normally, in cupboards. There will normally be no need for fire detection within roof voids, unless there are specific, significant fire hazards within a roof void, such as gas boilers or electrical equipment for photovoltaic systems. All smoke detectors within circulation spaces, or areas into which kitchens open, should be of the optical type; alternatively, appropriate multi-sensor detectors may be used. In single storey premises and other premises with no more than four bedrooms (including staff bedrooms), fire detection may comprise a Grade D system, as defined in BS 5839-6: 2013 (i.e. the detectors may comprise mains-operated domestic smoke alarms with internal standby batteries or capacitors). All smoke alarms should be interlinked by either wiring or radio transmission, so that, when fire is detected by one smoke alarm, all smoke alarms in the property sound simultaneously. Unless there isat least one member of staff present (whether awake or asleep) on a 24-hour basis, the standby batteries should be tamper proof (e.g. cells soldered to a printed circuit board, capacitors or PP3-type batteries that are fixed in place and cannot readily be removed). In premises of two or more storeys with more than four bedrooms (including staff bedrooms), domestic smoke alarms should not normally be regarded as adequate. The fire detection in these premises should comprise a Grade A system, as defined in BS 5839-6, with control and indicating equipment sited within the ground floor circulation space, fire detectors and fire alarm sounders. Where there is, at any time, less than two members of staff on duty, either the system should be addressable or there should be remote indicator lamps outside the entrance door to each resident’s accommodation, so that the location of a fire can be quickly identified. However, if existing premises of not more than two storeys are provided with sufficient mains-operated smoke alarms (with standby batteries or capacitors), these need not be replaced with a Grade A system until the smoke alarms reach the end of their useful life.
-
Smoke detector in the staircase residential building
AnthonyB replied to a topic in Fire Alarm Systems
BS5839 Parts 1 & 6 for spacing, Building Regulations Approved Document B regarding only needing detection for smoke control, NFCC Simultaneous Evacuation guidance for where a purpose built block of flats does need an alarm system as well as LACORS for non building regs compliant conversions & many more sources! -
Bathrooms, unless containing a higher risk (e.g. boiler) don't usually require a fire door
-
Depending on who will be using the door (staff/public, under/over 60 persons) you should use either a BSEN 179 emergency exit device (https://www.safelincs.co.uk/emergency-bolts-and-push-pads/) or BSEN 1125 panic exit device (https://www.safelincs.co.uk/panic-bars-with-latches-or-bolts/)
-
Extinguishers servicing for a new job
AnthonyB replied to Brettkelly's topic in Fire Extinguisher Servicing
No - you just need to be competent and correctly equipped for the job which is currently accepted as holding an in date 4 day extinguisher technician qualification (renewed 3 yearly with a one day refresher), having the correct tools and consumables and of course insured. -
The test fire is the same and a plain water jet is a plain water jet. Operating pressures have risen slightly, but historically there was no need to push the test boundaries beyond 13A which was considered the equivalent of the old one 2 gallon water per 200 sq.yard rule from the pre rating days, whereas in more recent years a demand for higher ratings came in and as a 21A pass was generally achievable with a decent test operator so several manufacturers submitted models for the 21A test
-
I would suspect the work was done without planning permission or Building Regs approval so the local Council is the first step
-
Report it to the fire service for the fire safety risk and the Environmental Health or HSE (Depending on the industry) for the H&S risk - assuming whoever is responsible for the stairs knows about it and has failed to act.
-
No it doesn't - once you are in the protected route it should lead to a final exit and so travel distance is to a large sense irrelevant - otherwise you would never get a building over 6 floors. Also it's only 45m where escape is available in 2 directions, 18m in a single direction (figures differ slightly for different usages and risk levels)
-
They will be talking about the elements of the communal system required in the building - there should be a common system in addition to the individual smoke alarms to each flat and this common system includes alarms/detectors in each flat As you are the freeholder responsible for the common areas under the Fire Safety Order and Housing Act you are responsible along with the other owner for the above systems being implemented. If he won't contribute his 50% of the costs it's a civil legal matter between you and him, but if nothing is provided you both risk crimina proceedings under Housing and Fire Safety legislation.
-
Fire/Heat Alarms in 2-Storey Flats with Separate Entrances
AnthonyB replied to John Lucas's topic in Fire Alarm Systems
With one system, yes. However there should be two systems, a communal one & an individual flat one. The common system only needs heat detectors in the flat as it's there to detect fire before it breaks out of the flat and not to save the occupiers of the flat of fire origin, the heat detector will not false alarm from cooking, etc. This avoids every flat being disrupted by false alarms, only genuine ones. (the detectors in this system to any internal common areas would be smoke) The flats then still need a system to safeguard the occupiers, using smoke alarms - but these aren't linked outside the flat so the only people disturbed by false alarms are in one flat -
Foam is actually far more predominant in the UK and has been for 30 years and is only just slowly changing. There is a lot of history to this too going back to the 1980's. Extinguisher provision for flammable solids (Class A) is based around the the Class A floor rating (sq.m. x 0.065) using enough extinguishers to cumulatively meet the rating. The normal fire rating for a 9 litre water jet extinguisher was 13A, suitable for 200sq.m. per unit. However these were heavy and bulky and some companies wanted to use lighter 6 litre units, but these were only rated 8A so they had to buy twice as many. Also electrical equipment was becoming more and more predominant. Enter the AFFF Foam Spray extinguisher, first developed in the UK in 1978/9 which from a 5.5l could get a 13A rating, meaning you could use a smaller easier to use extinguisher without needing to double up. It also had an 89B (later 113B & 144B) rating for flammable liquids and unlike the traditional water jet had passed the 35kV electrical conductivity safety test of BS5423 (our manufacturing standard prior to adopting EN3) allowing a margin of safety if used on electrical fires. As a result it became popular as a lightweight multipurpose extinguisher, widely adopted in the 80's by several large companies & retail chains as well as British Rail and becoming the standard stock item of extinguisher service companies being installed as a standard item for A risks, regardless of any Class B risk. The 90's saw the introduction of water spray (plain & with additive) extinguishers that also were able to achieve 13A ratings from smaller extinguishers as well as having the electrical conductivity pass - but the use of foam was so ingrained in the fire trade that they were slow to be adopted. The environmental impact of foam (& the likelihood that fluorine free environmentally acceptable replacements to AFFF will be much more expensive) and phasing out of the commonly used foams means that water is making a resurgence and starting to become far more common. The trade is slow to change though, hence why innovations such as Water Mist haven't taken off as much as they should. The trade and it's influence on standards also explains the large number of CO2 extinguishers in the UK as unlike the rest of Europe they refuse to acknowledge that a EN3-7 35kV test pass means the extinguisher is safe to use on electrical fires up to 1000V allowing them to double sales by putting a CO2 with almost every other extinguisher. If we followed the US approach you would just see Powder everywhere, but the UK has a history of using the best extinguisher for each fire class rather than a multipurpose approach.
-
Is this rigid foam insulation flammable? or fire-rated?
AnthonyB replied to Rachel's topic in Fire Prevention
It's also deprecated as a form of insulation now as it causes all sorts of problems in the house below. With no test certificate it's difficult to say. -
AFD in 2 / 3 storey converted house into flats
AnthonyB replied to Richie H's topic in Fire Alarm Systems
The mixed system as per LACORS is still appropriate, just allowing for the changes in the newer BS5839-6. LACORS is under review as it needs refreshing, but this seems to have stalled. -
Whilst a Euroclass B-s1.d0 rating means it's combustible it also means it has: -Little or no contribution to fire. - The material contributes little or insignificantly to the development of smoke. – The material does not create flaming particles or droplets when subjected to fire and considering the height of the structure and that it is only attached to your house shouldn't be an issue. This situation is one of the many traps of buying new developments as leaseholds sadly
-
There's no automatic requirement to separate kitchens in this way and open plan is used in many cases - it's still of use for property protection and in some situations could be necessary for life safety - if you feel the layout of the premises is such the fire separation is important for the safety of relevant persons then it's appropriate to recommend it.