-
Posts
2,486 -
Joined
-
Last visited
Everything posted by AnthonyB
-
If you mean the LED that indicates there is a mains supply entering the fitting and the battery charger is active then it's not an individual part - you need a new fitting.
-
Depends on the location of the exit and any external escape routes passing it, but it's possible most of the time.
-
Is there an external stair adjacent? Is the walkway only allowing escape in one direction so you have to pass the door? Is the walkway narrow so you have to pass by the door or within a metre of it so there would be no avoiding any smoke/flame/heat? If the answer to any of these is yes then the external door should be a self closing fire door.
-
There's nothing to stop a fire exit route being used as a normal access route from a fire safety legislative point of view as long as it remains clear of obstruction, free from combustibles (usually if indoors), and readily available for use. It shouldn't be bolted if a dedicated fire route - I think the resident is using all this as an excuse to keep the area to themselves.
-
Do flat owners under their own management need fire risk assessment?
AnthonyB replied to a topic in Fire Alarm Systems
The FRA should be for the block, not the individual flat. Unfortunately from experience it could come up with a wide range of outcomes from no action/minor actions to substantial risks and significant remedial actions. The responsible person would be required to remedy this - usually the freeholder or resident's management company depending on how the block is owned. -
It doesn't sound healthy! I'd want that checked by an electrician.
-
Generally yes, but like with purpose built flats it depends on the size and layout - it's not an across the board approach and certain scenarios, even in purpose built, still require upgrade or replacement of doors.
-
That's a drop over 300mm so the creation of the drop doesn't comply with Building Regulations, would breach the Workplace (Health Safety & Welfare) Regulations and will get the no win no fee compensation lawyers lining up to take the case when someone falls off it! Hardly a safe means of escape either.
-
Existing Dwellings protected stairway enclosure
AnthonyB replied to Kevin99's topic in Fire Risk Assessments
You are using the incorrect guidance - BS9999 is not for flats and is for designing new non domestic buildings. Blocks of flats have far more onerous smoke control requirements due to their fire strategy being of stay put. Existing flats should be assessed to this guide (& then it's impending replacement) https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/1020410/Fire_Safety_in_Purpose_Built_Blocks_of_Flats_Guide.pdf -
https://ligtas.co.uk/online-course/fire-marshall-awareness
-
There is nothing stopping you locking this door, although it would be advisable to have a lock that can be opened from the inside without a key to allow emergency escape. The fitting of the lock should not compromise the integrity of the fire door so should follow the door manufacturers instructions.
-
Single 12.5mm plasterboard with a plaster skim used to be the standard for 30 minutes fire resistance a long time ago but the current manufacturers guidance based on testing is that you now need to use 2 x 12.5mm. However there are different material combinations for different situations, the British Gypsum White Book (https://www.british-gypsum.com/specification/white-book-specification-selector/white-book-overview) is a useful reference. You should contact your Building Control department as they will have a minimum spec they will accept.
-
Chairs in village hall without fire retardant label
AnthonyB replied to Scotia's topic in Passive Fire Protection
Commercial use is different to domestic - guidance is here https://www.fira.co.uk/technical-information/flammability/fire-safety-of-furniture-and-furnishings-in-the-contract-and-non-domestic-sectors -
The requirement for internal fire doors to self close in dwellings was removed a long time ago so the previous occupier will have legitimately removed them. You should of course try and keep the doors closed where possible, especially at night.
-
If they are on an internal door you can cut the chains - it used to be a requirement to fit these a long time ago, but this was dropped some years ago.
-
Grade F systems only have a single power supply and are more prone to removal and failure. The robust nature of a Grade D system is why it is now the norm and the use of Grade F equipment is being phased out slowly as legislation requires more and more places to have Grade D (or higher) when built, rewired or altered. Wireless linked systems are the norm and the old need for linking physically with bell cable is long gone
-
HI, For full detail you would need to appoint someone to prepare such a specification but to avoid you ending up with over provision: - Your description suggests the conversion will comply with the current edition of Approved Document B or BS9991 with the requisite fire compartmentation - This in turn suggests a stay put approach - Flats would have their own separate & self contained smoke/heat alarms to BS5839-6 - You do not need any form of common fire alarm system - You only require smoke detectors to open the smoke vent, no sounders, no call points - Despite it being common (& lucrative) practice there is no need to provide a separate fire detection system to activate the vent - there are several manufacturers of smoke vent equipment where all the required detectors, manual controls, etc can be directly connected the the vent controls with out the need for a fire alarm control panel etc - One example: https://aov-direct.co.uk/product/ventec-ostro-1m2-gfa-stairwell-aov-kit/ - This way you won't have to pay for installation of and pay for ongoing testing of equipment you don't need, just the smoke control system and no unnecessary components that aren't correct for stay put.
-
30 minutes protection would usually be accepted and you could potentially uprate the existing cupboard using intumescent card, paper or paints
-
Victorian house, converted into flats in 1980s
AnthonyB replied to Ian W's topic in Fire Risk Assessments
The FRA would consider if the upper floors are at risk from a fire in your flat, i.e. if you have sufficient fire separation. -
How can you stop children from a childcare centre leaving through a fire exit?
AnthonyB replied to a topic in Fire Exits
Locking isn't usually OK if it requires reliance on a code or key. Kitchens are dangerous environments for children and I'd be more worried that they got in the kitchen and that door should be the first point of concern - child gates, access control, etc -
Fire Alarm System for 3 storey owner owned flats.
AnthonyB replied to Rod's topic in Fire Alarm Systems
The premises require a Fire Risk Assessment which should answer this - a key factor is the fire compartmentation or otherwise which will have a big impact on what, if anything, is required -
https://www.asfptraining.org.uk/
-
No, there is no requirement for any interaction, the commercial system can be self contained.